I'm doing LEED certification, when I run Apache Sim appear one window with "Error: Material CVTY0083 not found".
The software generate this error only after importing Prototipe Data (ASHRAE Baseline).
Also if in building template manager I try to import external Template appear another one error window: "corrupt construction database:construction BSWAL42 refers to missing material CVTY0083. Please inform IES Ltd"
What's wrong?
Thanks in advance
Error: Material CVTY0083 not found
-
simonemiri3
- VE Newbie

- Posts: 7
- Joined: Tue Oct 15, 2013 8:09 am
Re: Error: Material CVTY0083 not found
It’s caused by baseline wood framed walls. If this is a prm project, the walls should be metal framed so you should either delete these constructions or open each wood framed baseline construction and remove the composite layer. If you do need these constructions for the proposed perhaps, you can use the ASHRAE wizard in the tools menu of the constructions database to create it.
Just open the constructions database, look for any baseline construction with wood frame in the name, select using the check box and click delete or open each of them and delete the composite layer.
Just open the constructions database, look for any baseline construction with wood frame in the name, select using the check box and click delete or open each of them and delete the composite layer.
-
simonemiri3
- VE Newbie

- Posts: 7
- Joined: Tue Oct 15, 2013 8:09 am
Re: Error: Material CVTY0083 not found
I solved the problems!
Thanks,
Simone