First off i'd like to point out that Criterion 3 is a solar gain check and not purely overheating. This is described in detail in the
NCM modelling guide.
Basically what happens is a benchmark solar gain is calculated for each space following the guidance in paragraphs 114-116 . It is important to note that the benchmark
is not the solar gain for the space in the Notional building. This benchmark is then compared against the solar gain for the same space in the actual building. If the solar gain for the space in the actual building is higher than the calculated benchmark then you fail the criterion 3 check for that room.
As you are using SBEM it is very difficult to troubleshoot this issue as it is SBEM itself which calculates both the solar gain in the actual building and the benchmark. If you feel it is incorrect then all I can recommend is sending your project input file to the sbem helpline
sbem@bre.co.uk and ask them to have a look.
To find the input file select Building Compliance and then View Results folder.
The input file will have the building name and the extension .inp (eg. examplebuilding.inp). You can ignore the BRUKL and notional building input files.