Please help - Weird Room Temperature Values!

Post by ivan_pqs »

Hi Brain trust, really need your help here.

Referring to this pic https://drive.google.com/file/d/15ltCn3 ... sp=sharing, node 350 shows temperature of 9C whereas node 351 shows temperature of 23.5C

The zone temperature is expected to be lower than 23.5C. However, in VistaPro, the zone temperature displays 36C and high humidity as seen in https://drive.google.com/file/d/15h98GX ... sp=sharing . What could be the possible issue?



Cheers,
Ivan
gazzat5
VE Beginner
VE Beginner
Posts: 12
Joined: Tue Jul 09, 2019 9:53 am
Location: London
Contact:

Re: Please help - Weird Room Temperature Values!

Post by gazzat5 »

Hi Ivan,

Can you please share a screenshot of your apachehvac network?
Or better, the .ASP file?

Also, if you need faster help, you're better off contacting IES technical support at: support@iesve.com ;)
But don't forget to post the solution here for others in the future ;)
tanveer
VE Newbie
VE Newbie
Posts: 3
Joined: Tue Nov 08, 2022 1:13 pm
Location: GB
Contact:

Re: Please help - Weird Room Temperature Values!

Post by tanveer »

HI Ivan,

Node 350 shows the average supply air temperature to zones while 351 shows the average return air temperature from zones.

36C is the average temperature of all the rooms inside the zones. This can be different than Node 351 depening upon the airflow to each room in the zone.

Check if any of the room has high temperatures due to some reason (no setpoint, inadequate airflow or coil capacity)