I need to run PartL Compliance calculation via DSM method for naturally ventilated building , I am using the same model that I created for the purpose of overheating assessment , all openings (including windcathers) are controlled by temperature and CO2 , My observation is when I link macroflow for DSM calculation ; i realised that the carbon emission from the building increases (against the option without macroflow linked) I understand that the heating energy will increase as a result of control strategy of the openings so I cannot see any benefit of linking macroflow as the software already assign natural ventilation rate for zone that are either not air-conditioned or mechanically ventilated , so i assume I am doubling natural ventilation losses ( one from the vent rate attached due to activity type , and one from macroflow) my question is within the legal frame of UK compliance and EPC calculation , although i use macroflow for overheating calculation ; do I still need to link or use macroflow in DSM calculation ? would it be ok to issue epc without this linked?
My Comment as follows
I understand that having macroflow linked will help cooling energy and it will reduce internal temperature due to benefit of actual vent control strategy (temperature control ) however it will also increase heating load because of heat loss from macroflow opening , If there is no legal requirement to use this option in the dsm calculation , I would think to not use macroflow unless it provided positive benefit ( like energy reduction from cooling becomes greater than energy increase in heating , so overall carbon emission reduces)