Air Exchanges

Post by iwmech »

A quick one, does anyone know what l/s.m²fac mean as a unit for air exchange flow rate?

Thanks in advance.
User avatar
Complex Potential
VE Expert
VE Expert
Posts: 467
Joined: Wed Jan 09, 2013 11:57 am
Location: Bristol, UK

Re: Air Exchanges

Post by Complex Potential »

That just means that the flow rate is dependent upon the floor area of the room the air exchange is attached to.

So if you have a template with an air exchange set at 0.5 l/s.m2 and you apply that template to a room with 50m2 floor area, the flow rate for that room will be 0.5 x 50 = 25 l/s

CP
iwmech
VE Newbie
VE Newbie
Posts: 8
Joined: Thu Jan 09, 2014 1:37 am

Re: Air Exchanges

Post by iwmech »

Hi CP,

Thanks for your response. Thought about it some more and I suspect that it actually means L/s per meter squared of facade? There is another option L/s.m^2 and I guess this is what you suggested.

Thank you.
User avatar
Complex Potential
VE Expert
VE Expert
Posts: 467
Joined: Wed Jan 09, 2013 11:57 am
Location: Bristol, UK

Re: Air Exchanges

Post by Complex Potential »

Ah yes, I think you're right. That one is quite a new option I think but handy.