Can't select VSD's on my pumps. Aux Energy is through the roof

VE-SBEM for compliance and EPC generation.
Post Reply
barrywalsh
VE Newbie
VE Newbie
Posts: 1
Joined: Tue Apr 08, 2014 3:24 pm

Can't select VSD's on my pumps. Aux Energy is through the roof

Post by barrywalsh »

I am doing an SBEM calc for a pharmaceutical project and my Aux Energy is through the roof, I assume this is to do with the fact that I can't select VSD's on my pumps because of the centralized system I have chosen. Is there a way around this?
User avatar
Terence
Site Admin
Site Admin
Posts: 411
Joined: Mon Aug 25, 2008 12:58 pm
Location: Glasgow, UK
Contact:

Re: Can't select VSD's on my pumps. Aux Energy is through th

Post by Terence »

Some system types do allow for variable speed pumping.

The specification of which HVAC system can be defined with variable speed pumping is part of the NCM as listed in Table 10 of the 2010 NCM Modelling Guide, which is available for downloaded from the NCM website.
Terence McMahon
IES Technical Support
Linkedin
ecoboost
VE Student
VE Student
Posts: 39
Joined: Thu Aug 15, 2013 6:32 am

Re: Can't select VSD's on my pumps. Aux Energy is through th

Post by ecoboost »

select a system type that allows variable speed pumping, don't know why they restrict you to constant speed
JohnLloyd
VE Professor
VE Professor
Posts: 173
Joined: Tue Oct 05, 2010 8:51 am

Re: Can't select VSD's on my pumps. Aux Energy is through th

Post by JohnLloyd »

I've never fully understood why it's restricted to certain system types. The vast majority of the air based heating and cooling systems we design are variable volume systems. It's another bizarre quirk of the NCM that appears to be simply incorrect that would extremely easy to fix, but has never been.

I haven't checked but presume this hasn't changed for the 2013 regs?
User avatar
Complex Potential
VE Expert
VE Expert
Posts: 467
Joined: Wed Jan 09, 2013 11:57 am
Location: Bristol, UK

Re: Can't select VSD's on my pumps. Aux Energy is through th

Post by Complex Potential »

If your aux energy is through the roof then I suspect you are using a variable volume/constant volume system? Unfortunately any centralised system is going to get hammered on the aux energy due to having to size fans for room loads. The pumping makes almost no difference in comparison.