CHP

Part L2 of the Building Regulations (2006 edition).
Post Reply
bootsam
VE Professor
VE Professor
Posts: 184
Joined: Fri Sep 10, 2010 1:15 pm

CHP

Post by bootsam »

I'm not seeing any energy on the BRUKL for CHP. Ive added it via the renewables tab and ticked it via the NCM template manager. I'm running a LTHW with rads scheme and would expect to see CHP energy on the BRUKL but I am not. Am I being stoopid? :D
bootsam
VE Professor
VE Professor
Posts: 184
Joined: Fri Sep 10, 2010 1:15 pm

Re: CHP

Post by bootsam »

I reduced the rated output to only 1kW from the default 1000kW and now I am seeing CHP on the BRUKL. Whysat?

Upped it to 250kW and now its dissappeared again? WTF?
bootsam
VE Professor
VE Professor
Posts: 184
Joined: Fri Sep 10, 2010 1:15 pm

Re: CHP

Post by bootsam »

Figured it. Min output it shuts down before unit sees benefit as its so small.

I have an energy centre providing energy for 400+ dwellings and 1 small retail unit. Thus when I shove the huge 400kW CHP on, the min 0.5 is 200kW and my small load is too small to be seen.

Just posting this for others information.