Hi,
Thanks for your interest. We're looking at what we can do to make these modules a little easier for people to use and will improve them when we can.
I'd probably point you towards the simulation calendar in APlocate to set up your holiday exceptions... however, a quick word on annual profiles.
To set up an annual profile you reference weekly profiles in sequence from the start of the year. It might be easier to think of each entry as: "Use this weekly profile up to the date I define here"
so 1 entry:
Weekly profile ----------------End Month---End Day
Occupancy profile 1 -----------Dec ------ 31
means use Occupancy Profile 1 for the full year.
now, setting up for a simple summer/winter schedule we could have something like this:
Weekly profile ----------------End Month---End Day
Winter schedule -----------May ------ 31
Summer schedule -----------Sep ------ 30
Winter schedule -----------Dec ------ 31
Very basic and perhaps overly simplistic but I hope it gets the point across.
Have a read here for a little more:
http://www.iesve.com/downloads/help/Thermal/APPro.pdf
Also, pop on to one of the web overview sessions run by
training@iesve.com and I'm sure they can help out.
- David.