Hello everyone !
I get trouble with my model. I am using the IESVE version 2014.1.0.0
I build an office with a 19°C heating setpoint, a natural night ventilation. This freecooling makes my results having bugs.
When I observe this variables simultaneously in VistaPro :
1)Resultant temperature
2)Macro flow ext vent gain
3)heating plant sensible loads,
4) Dry bulb temperature
I observe completely unrealistic values.
1) My dry resultant temperature is around 64°C which is impossible,
2) My macroflow ext vent gain is around -420 kW,
3) My Heating plant sensible load is around 440 kW , because I have lost 420 KW with my freecooling which is impossible...
4) My dry buld temperature which is my outside temperature is correct and around 5 °C.
My opening scenario is :
gt(tdr,22,0.5) & gt(ta,to,0.5) (windows open from 0:00 to 24:00 when Toperative inside >22°C and Temperature inside > Temperature outside).
Here you can see the image of my results
<img src="C:\Users\xavier.cattelain\Desktop\Iesve_overheating">
Respectfully
Overheating when cooling with natural ventilation
- Complex Potential
- VE Expert

- Posts: 467
- Joined: Wed Jan 09, 2013 11:57 am
- Location: Bristol, UK
Re: Overheating when cooling with natural ventilation
This looks like your window opening is far too big and too much cold air is entering the room. As a result your heating system is hammering up to compensate because you have it set to unlimited. The dry resultant temperature is shooting up because your heating system has a radiant component to it by default (0.2 I think unless you've manually changed it).
Essentially you have a massive convective heater fighting against the wide open window trying to keep the air temperature at 19C, but it is also acting as a giant radiant panel, frying anyone nearby.
Try dropping the free area of the window openings or set a limit on the heating system or set the heating radiant fraction to zero, or possibly all three.
CP
Essentially you have a massive convective heater fighting against the wide open window trying to keep the air temperature at 19C, but it is also acting as a giant radiant panel, frying anyone nearby.
Try dropping the free area of the window openings or set a limit on the heating system or set the heating radiant fraction to zero, or possibly all three.