Revit import problem in terms of balcony slabs

Post by zaferyuce »

Heallo all,

I have modelled a sample building in Revit and exported as gbXML file for IES VE. However balcony slabs are missed in IES modelIT tab.

Do you have any idea about this?

Regards.
User avatar
PCully
Site Admin
Site Admin
Posts: 1465
Joined: Tue Sep 09, 2008 9:52 am

Re: Revit import problem in terms of balcony slabs

Post by PCully »

Hi,

I don't think a balcony slab will be exported from Revit to the gbXML as they are not room bounding. The white paper guidance we have developed discusses this and also the export complexity options which you should check to ensure you have shading surfaces included in your gbXML export/import.

http://www.iesve.com/support/knowledgebase/faq/3051

Phil