NCM heating energy (MWh) NCM cooling energy (MWh) NCM auxiliary energy (MWh) NCM lighting energy (MWh) NCM DHW energy (MWh)
Date a_Model With Ceiling Voids.aps a_Model With Ceiling Voids.aps a_Model With Ceiling Voids.aps a_Model With Ceiling Voids.aps a_Model With Ceiling Voids.aps
Jan 01-31 25.6022 0.0504 18.6901 24.6910 21.6375
Feb 01-28 22.2026 0.0376 16.9844 19.4672 19.6690
Mar 01-31 15.3797 0.1949 18.6901 17.8091 21.6375
Apr 01-30 12.0364 0.6142 16.2586 12.9073 18.7143
May 01-31 3.0146 7.1087 17.8917 12.7327 20.6659
Jun 01-30 0.3514 8.3920 17.8554 12.2790 20.6575
Jul 01-31 0.1803 11.9624 18.6901 12.7334 21.6375
Aug 01-31 0.2854 11.2567 18.6901 13.8358 21.6375
Sep 01-30 1.4794 5.9264 17.0570 14.6975 19.6859
Oct 01-31 6.6328 1.8926 19.4885 21.0110 22.6091
Nov 01-30 16.6455 0.0530 18.6538 23.5819 21.6291
Dec 01-31 19.3443 0.0169 16.2949 22.4796 18.7228
Summed total 123.1545 47.5058 215.2448 208.2254 248.9037
Sorry heres an update i was looking at the wrong results.
Heating = 123
Cooling = 47
Aux = 215
lighting = 208
DHW = 248
there quite different from what i quoted above
Like your saying dhw is quite high. seems kinda crazy that its twice the heating demand of the building
Apache DSM for Part L2 (2013) not picking up shading
-
wyliecoyote
- VE Student

- Posts: 40
- Joined: Thu Jan 22, 2015 3:26 pm
- Complex Potential
- VE Expert

- Posts: 467
- Joined: Wed Jan 09, 2013 11:57 am
- Location: Bristol, UK
Re: Apache DSM for Part L2 (2013) not picking up shading
Ok, no problem. The cooling is still a small player as I suspected.
Looking at those numbers, it's not worth troubling yourself over the cooling. If I were you, instead of adding shading, I'd be focusing on lighting and fan powers and maybe trying to shave a little off the space heating side. The DHW is normally quite tricky to influence much but you never know your luck.
Looking at those numbers, it's not worth troubling yourself over the cooling. If I were you, instead of adding shading, I'd be focusing on lighting and fan powers and maybe trying to shave a little off the space heating side. The DHW is normally quite tricky to influence much but you never know your luck.
-
wyliecoyote
- VE Student

- Posts: 40
- Joined: Thu Jan 22, 2015 3:26 pm
Re: Apache DSM for Part L2 (2013) not picking up shading
Excellent, very very informative 
Thanks again for your help, its extremely useful!!!!!
Thanks again for your help, its extremely useful!!!!!