Building Floor Area

Post by hlehmann »

Hi,

I'm trying to run a CIBSE Loads calc on the model, but it doesn't account for all the rooms in the model (only 1 room) although these are ticked as 'include to the building floor area' section under Room Data. Also all rooms were selected prior clicking the CIBSE Loads button.

Image
wyliecoyote
VE Student
VE Student
Posts: 40
Joined: Thu Jan 22, 2015 3:26 pm

Re: Building Floor Area

Post by wyliecoyote »

Hi,

Hopefully i can be of some assistance.

It looks as if that one room could be set as an "adjacent building".

Reason im thinking this is that in the image you provided it has a pink outline signifying an "adjacent building".

If this is so, just right click the space and change the room in the properties.