While working through the PRM, I am stuck at step "Assign Sizing.." which comes after Room Load Calculation step. The error which appears says that
"No Baseline Calculation Found...etc"
Did anyone face the same issue? Is there a way to resolve it?
PRM Sizing Run Issue
Re: PRM Sizing Run Issue
Hi,
This error (no baseline calculations detected) would be triggered when the Proposed system loads data spreadsheet does not exist in the project folder.
Most typical reason for this - no prototype autosizable system shave been imported and assigned in your proposed.asp ApacheHVAC network.
Phil
This error (no baseline calculations detected) would be triggered when the Proposed system loads data spreadsheet does not exist in the project folder.
Most typical reason for this - no prototype autosizable system shave been imported and assigned in your proposed.asp ApacheHVAC network.
Phil
IES Worldwide Technical Support