Condensation Analysis

Post by mech student »

Hi all,

I would like to ask if the software calculates interstitial condensation or room condensation cause i am not sure which of the two it is referring to.

Thanks
User avatar
PCully
Site Admin
Site Admin
Posts: 1465
Joined: Tue Sep 09, 2008 9:52 am

Re: Condensation Analysis

Post by PCully »

Hi,

The condensation analysis feature in VE is found in the Constructions database, it is a steady state calculation to assess risk of condensation through a construction makeup for given internal and external conditions.

There are notes in the Constructions Database User Guide (Help >> User Guides >> Thermal)

Phil
IES Worldwide Technical Support
jholgate
VE Beginner
VE Beginner
Posts: 15
Joined: Wed Aug 26, 2009 12:32 pm

Re: Condensation Analysis

Post by jholgate »

I have just been carrying out an interstitial condensation risk analysis and the link below, taken from a previous post, suggests VCL membranes have resistivity of 120 with foil going to around 4000 max. These would be the values directly entered into the constructions in IES.

http://www.engineeringtoolbox.com/vapou ... _1807.html

However, I believe polythene should be more like 2,000,000 using a thickness of 0.1 to 0.3 mm. Can anyone clarify as its difficult to get accurate data. I have a value of 700 MNs/g for a 0.3mm membrane which becomes 2,100,000 MNs/g.m (or GNs/kg.m) at this thickness.

Thanks