Hi,
I've noticed that the baseline model, when generated, does not include the adjacent buildings drawn in the proposed model. Is there a way to include these since I can't seem to be able to use ModelIT on the baseline model to modify it in any way.
Thanks!
Baseline model doesn't include adjacent buildings
Re: Baseline model doesn't include adjacent buildings
Hi,
I believe the 2007 Navigator will exclude any shading objects whereas the 2010 Navigator should retain these in the Baseline building so they can be include din SunCast solar shading calculations
Phil
I believe the 2007 Navigator will exclude any shading objects whereas the 2010 Navigator should retain these in the Baseline building so they can be include din SunCast solar shading calculations
Phil
IES Worldwide Technical Support
-
farahghanem
- VE Professor

- Posts: 147
- Joined: Tue Sep 08, 2015 8:41 am
- Location: Abu Dhabi
- Contact:
Re: Baseline model doesn't include adjacent buildings
Just as phil said, ASHRAE 90.1-2007 requires that no shading effects are considered for the baseline, unlike ASHRAE 90.1-2010