more than one construction type for same external wall

Post Reply
alisyed
VE Newbie
VE Newbie
Posts: 7
Joined: Mon Oct 26, 2009 11:00 am

more than one construction type for same external wall

Post by alisyed »

Hi.

I have already build the model, but the architect has now changed the external wall constructions. Now there are two different types of constructions for some external walls.
How can I assign two different types of constructions to same external wall.

Thanks
User avatar
PCully
Site Admin
Site Admin
Posts: 1465
Joined: Tue Sep 09, 2008 9:52 am

Re: more than one construction type for same external wall

Post by PCully »

Hi,

You can do this by splitting the room in ModelIT (use the Divide Space tool and make sure you select the "Divide without partitions" option), this will split the room into as many sections as you like. Then when assigning Constructions select the room and go down the levels of decomposition to select the individual surfaces you want to edit and use the Assign Constructions dialog as normal to replace what's already assigned. Hope that helps.

Phil
IES Worldwide Technical Support