I'm modelling a low-energy dwelling built on passivhaus principals. We expect the planned triple glazing (http://bit.ly/bdgXt3 or similar) to achieve a U-value of around 0.8W/m2K (with a lower Ug-value). Any tips on how to best reflect this in the IES contructions?
I seem to have hit a limit of Ug = 1.73 W/m2K using two 6mm clear floats and a 6mm pilkington, with 12mm argon-filled cavities.
Thanks
low-energy glazing - constructions database tips?
Re: low-energy glazing - constructions database tips?
I've not had time to check it out yet but I believe LBL labs (the guys that gave us Radiance) have a glazing tool that shows virtually any glass in a format that can be directly used to create ies windows... might be worth having a play.
Re: low-energy glazing - constructions database tips?
I solved this a while back, but for anyone else stuck trying to get lower u-values:
The trick is in the emissivity of the inside and outside surface of each pane. Where the default for glass is something like 0.9, highly reflective coatings in the infra-red range bring it down to as low as ~0.03, and still leaves the emissivity in the visible light range high (~0.7). These values can be altered for each pane of glass in the window in the constructions menu.
Tom
The trick is in the emissivity of the inside and outside surface of each pane. Where the default for glass is something like 0.9, highly reflective coatings in the infra-red range bring it down to as low as ~0.03, and still leaves the emissivity in the visible light range high (~0.7). These values can be altered for each pane of glass in the window in the constructions menu.
Tom
-
huntervu28
- VE Graduate

- Posts: 68
- Joined: Mon Oct 05, 2009 1:56 am
Re: low-energy glazing - constructions database tips?
Change cavity resistance to meet your demand, this tip is in <VE> official document, not my trick .
Re: low-energy glazing - constructions database tips?
- really? it's odd that they recommend modelling broken physics, when it can actually handle low-e glazing just fine without bending the rules!huntervu28 wrote:Change cavity resistance to meet your demand, this tip is in <VE> official document, not my trick .
Re: low-energy glazing - constructions database tips?
Hi there,
Would anybody be able to help here by suggesting some glzing properties that can be considered as 'low-e' and also another set of properties for 'reflective' glazing? I'm just trying to model some options that are possibly suitable for hot-arid climates.
I have come across some suggestions here i.e. changing the air gap resistance but not sure which values are reasonable.
Any advice is highly appreciated.
Yahya
Would anybody be able to help here by suggesting some glzing properties that can be considered as 'low-e' and also another set of properties for 'reflective' glazing? I'm just trying to model some options that are possibly suitable for hot-arid climates.
I have come across some suggestions here i.e. changing the air gap resistance but not sure which values are reasonable.
Any advice is highly appreciated.
Yahya