CO2 concentration starts before people

Post by KasperS »

Hello

I have noticed in my calculations that the CO2 concentration starts to rise 30 min before the people arrive in the room. I spoke with a co-worker and she experienced the same in her models. Is there a reason for this and can it be eliminated?

From Kasper
KasperS
VE Professor
VE Professor
Posts: 115
Joined: Tue Apr 19, 2011 7:56 am

Re: CO2 concentration starts before people

Post by KasperS »

hey

I am using 2 min intervals, so that shouldnt be the problem. :)

From Kasper
User avatar
PCully
Site Admin
Site Admin
Posts: 1465
Joined: Tue Sep 09, 2008 9:52 am

Re: CO2 concentration starts before people

Post by PCully »

Hi,

I haven't hear of this before, did some quick test sims with different time steps and reporting intervals but still didn't see this problem (I was using a 9-5 occupancy profile and Room CO2 didn't rise until 9 each time). You don't have your occupancy on a ramp profile or anything that might kick in before 9?

Only other area having an impact I can think of is MacroFlo, maybe try running with MacroFlo off, reduced number of rooms until you find the cause of the anomaly.

Phil
IES Worldwide Technical Support
KasperS
VE Professor
VE Professor
Posts: 115
Joined: Tue Apr 19, 2011 7:56 am

Re: CO2 concentration starts before people

Post by KasperS »

Hey

I tried to test it if it was MacroFlo, but it did not help. I also tried to turn off HVAC.
I talked with another co-worker who did his master thesis using IES. He also said he encountered the problem, and IES gave him some long explanation, but he can't remember it anymore.