Well, kind of.st_george wrote:.... This means, that in order to achieve the Lawson’s Comfort Assessment Criteria to be positive, the maximum wind velocity on the plaza, must not exceed 4 meters per second?
You have to prove that for 95% of the time that 4m/s is not exceeded. Due to the fact that CFD is so computationally expensive, and you can't analyse the wind environment around your site for a whole year, you must do some statistical analysis using local weather data.
You have also ignored the fact that Lawson's criteria addresses wind gusts as well. To be honest, I tend to ignore it as well, due to the difficulty in getting weather data of sufficient frequency to capture wind gust data.
So the way I go about it is....
1) find local weather data. The weather data in the VE is annual hourly data so for ease I would suggest using that. You may have to purchase weather data closer to your site than that bundled with the VE.
2) determine the annual mean wind speed from local weather data set
3) run 8 steady state CFD simulations modelling 8 wind directions at the annual mean wind speed, e.g. N,NE,E,SE,S,SW,W,NW. 16 would be more accurate, 4 less so.
4) determine the locations around your site where you want to calculate Lawson's criteria
5) find the wind speed at each of these locations for each of the wind directions. Hint: in Microflo use monitorings point to dump the CFD data to text file which you can open to find the wind speed at your locations. If you want to analyse 5 locations and have 8 wind directions this will mean you need to determine 5*8=40 wind speeds. This will need 5 monitoring points.
6) divide the 40 wind speeds from step (5) by the wind speed used for the Microflo sim (the annual mean wind speed) to determine a non-dimensional wind speed up factor
7) using the local weather data and the 40 wind speed up factors calculate the wind speed for each hour over the whole year for each of the 5 locations
8) determine the threshold wind speed at each of the 5 locations, i.e. the wind speed that for 95% of the year is below
I have written a program to do 7 and 8 which could save you a lot of effort. I will PM you.
Notes....
a) there is no method to calculate pedestrian comfort that has been set in stone as THE method to use, so you could come up with your own methodology if you can justify it to your clients
b) the use of steady state simulations and the k-epsilon turbulence model in Microflo ignores transient effects such as vortex shedding. To address this would need an LES turbulence model and a transient simulation. This is very expensive computationally and although it is best practice it is hardly ever done in our industry due to the fact (for isothermal flows) it is probably more expensive than basic wind tunnel testing
c) the wind speed up factor method ignore the fact that as Reynold's number (the ratio of inertial to viscous effects) changes then so does the flow regime (the path of the flow)



