Can anyone offer some good advise how best to measure fresh air distribution in a space using MicroFlo, as such to inform a judgement regarding indoor air quality a different points in the room. thanks all,
CFD Fresh Air Distribution
Re: CFD Fresh Air Distribution
How about using the age of air and air change effectiveness variables? Or if there are people in your model, the concentration of CO2?
-
Richardo1505
- VE Beginner

- Posts: 12
- Joined: Tue Mar 13, 2012 8:13 pm
Re: CFD Fresh Air Distribution
I'm not sure you can measure C02 with Microflo. I know you can with Macroflo
Re: CFD Fresh Air Distribution
You can. If your apacheSim/macroflo model has occupants then their CO2 production is automatically imported into Microflo and gets spread over the whole zone volume - from floor to ceiling height.
If you don't like that simplification you can add non-solid source components that release the same amount of CO2. Then you can control where the CO2 is released rather than use the default - over the whole zone.
If you don't like that simplification you can add non-solid source components that release the same amount of CO2. Then you can control where the CO2 is released rather than use the default - over the whole zone.
-
Richardo1505
- VE Beginner

- Posts: 12
- Joined: Tue Mar 13, 2012 8:13 pm
Re: CFD Fresh Air Distribution
ok thanks, I'll give it a go