hi everyone
i want to share this, and get some comments

if i chose window type that is 100% openable and has 0% frame, will that mean the window is 100% open and perform in the sim like there is no window at all? (like open option in Modle IT)

if that yes, we could use that instead of open option and calculate the MacroFlo in the Apsim

many thanks
User avatar
PCully
Site Admin
Site Admin
Posts: 1465
Joined: Tue Sep 09, 2008 9:52 am

Re: share idea !!

Post by PCully »

Yes, I think you are asking if you can set the window to be open 100% all of the time and in effect act like a hole, that's how to represent this for simulations (Apache won't allow a hole on an external surface so you have to use MacroFlo in this way).

Phil
IES Worldwide Technical Support