Auxilary energy starting 2 hours early?

Part L2 of the Building Regulations (2006 edition).
Post Reply
btysoe
VE Graduate
VE Graduate
Posts: 86
Joined: Fri Mar 01, 2013 9:39 am

Auxilary energy starting 2 hours early?

Post by btysoe »

I'm trying to understand auxiliary energy.

I've setup a single room building in this case a classroom heated by underfloor heating and a local MVHR unit providing ventilation.

Therefore the Auxilary energy is the sum of the pump power density and the fan power density multiplied by any PFC/metering correction factors applicable. I am fine with this and I can replicate the calculation arriving at the same result as IES. What I can't understand is why the auxiliary energy seems to start 2 hours before the ventilation kicks in? Any ideas? (see graph below)

Image
btysoe
VE Graduate
VE Graduate
Posts: 86
Joined: Fri Mar 01, 2013 9:39 am

Re: Auxilary energy starting 2 hours early?

Post by btysoe »

Thanks to Phil at IES support the answer is:

Auxiliary energy follows the plant profile which ramps up 2 hrs earlier. Whilst the ventilation follows the ventilation profile. Doesn't seem quite logical that there is a variation between the two, but that's the way it works. It is the same for the notional building.