Post by MarkHallman »

Hi there,

If I specify a series of data points in the part load curve dialog for a heating or cooling system, can anyone advise how the calculation handles a part load % that is in between two data points? For example, if I have 70 and 80% load but 73% is specified, would IES interpolate between these two data points or is there a step function that is applied, i.e., we would be at 70% load until 80% is reached?

Thanks!
Mark Hallman.
macleodd
IES Staff
IES Staff
Posts: 36
Joined: Wed Aug 27, 2008 1:33 pm

Re: Part Load Question

Post by macleodd »

Mark,
Apache would interpolate between the 2 data points.

Regards, Donald
IES Development Staff
MarkHallman
VE Beginner
VE Beginner
Posts: 18
Joined: Mon Aug 10, 2015 4:11 pm

Re: Part Load Question

Post by MarkHallman »

Thanks so much!