Edit System Parameters - Zone load oversizing factor
-
MatthewSteen
- VE Graduate

- Posts: 51
- Joined: Mon Nov 17, 2014 5:43 pm
- Location: Denver, CO, USA
Edit System Parameters - Zone load oversizing factor
Are incorrectly defaulted to 1.0 when importing PRM Baseline systems.
Building Performance Engineer | Ambient Energy | http://ambient-e.com/
Q+A Resource for the Building Energy Modeling Community | https://unmethours.com/questions/
Q+A Resource for the Building Energy Modeling Community | https://unmethours.com/questions/
-
farahghanem
- VE Professor

- Posts: 147
- Joined: Tue Sep 08, 2015 8:41 am
- Location: Abu Dhabi
- Contact:
Re: BUG: Edit System Parameters - Zone load oversizing factor
No, it is not incorrectly defaulted. You do not do Zone Load oversizing, you oversize the capacity of your equipment. The zone load oversizing serves a different purpose, such as if you are doing design informing modeling and want to take the "safety factor" that mechanical engineers typically do.

-
MatthewSteen
- VE Graduate

- Posts: 51
- Joined: Mon Nov 17, 2014 5:43 pm
- Location: Denver, CO, USA
Re: BUG: Edit System Parameters - Zone load oversizing factor
Thanks for the reply. So "Zone cooling load oversizing factor" and ""Zone heating load oversizing factor" boxes in the "Edit System Parameters" dialog are not the correct places to set this for the baseline? I maintain that if the VE doesn't do this automatically, it should for all PRM Baseline systems.
Building Performance Engineer | Ambient Energy | http://ambient-e.com/
Q+A Resource for the Building Energy Modeling Community | https://unmethours.com/questions/
Q+A Resource for the Building Energy Modeling Community | https://unmethours.com/questions/
-
farahghanem
- VE Professor

- Posts: 147
- Joined: Tue Sep 08, 2015 8:41 am
- Location: Abu Dhabi
- Contact:
Re: BUG: Edit System Parameters - Zone load oversizing factor
no its not the correct place. You should do that in the coil/chiller edit menu, and it is already defaulted there to the correct values.