Could you please tell me for making a dimming profile, where I must insert numbers( e1, 50, 1, 500 ,0.2 ) in the APpro
profile database?
User avatar
PCully
Site Admin
Site Admin
Posts: 1465
Joined: Tue Sep 09, 2008 9:52 am

Re: Making dimming profile

Post by PCully »

Hi,

I think this is also covered elsewhere but there is a good example in the ApPro user guide on page 34 http://www.iesve.com/downloads/help/ve2 ... /APPro.pdf
ramp(e1,0,1,500,.4) a formula suitable for applying as a dimming profile controlling lighting gain as a function of available daylight. It modulates the lighting gain as a function of the illuminance on the working plane, e1. The value of the profile falls from 1 at zero illuminance to 0.4 at illuminance 500 lux, thereafter remaining constant at this value. The value 0.4 (which you should set as appropriate) represents the fraction of the room‟s lighting gain which is not subject to daylight control. The illuminance e1 must be computed using the link to Radiance.
Phil
IES Worldwide Technical Support
Niki2001
VE Beginner
VE Beginner
Posts: 15
Joined: Thu Sep 13, 2012 2:53 pm

Re: Making dimming profile

Post by Niki2001 »

Many thanks for your help.