Hi Johnny,
In my limited experience I've found that inputting the SFP at system level should register on the BRUKL providing you've selected mechanilcal ventilation system as the 'primary system'. This figure as I understand it, is a figure for the total system, (Supply & Return) so there should be no need to go to room level and input a local supply or exhaust unless they're present.
If you DO input an SFP at room level, it should register on the BRUKL too under the 'local mecahnical supply & exhaust' section just after the main systems breakdon section, (Page 3 maybe). If you enter a SFP AND a flow rate for the exhaust, this doesn't register on the BRUKL for some reason, I don't know why. When I've done this and queried the relevant rooms in Vista, the system is taking account of the vent so it is in there somewhere. More clarity required though definintely
Let me know if you find anymore out about this as it seems to be widely misunderstood and gets numerous different responses when I ask people about it.
Cheers,
C