WAHP Fuel Limitation
If a WAHP does both cooling and heating, how is the energy allocated? It doesn't appear possible to allocate it to BOTH cooling and heating since the user can only select one fuel, e.g. "Electricity - Cooling" OR "Electricity - Heating". Am I missing something?
Building Performance Engineer | Ambient Energy | http://ambient-e.com/
Q+A Resource for the Building Energy Modeling Community | https://unmethours.com/questions/
Q+A Resource for the Building Energy Modeling Community | https://unmethours.com/questions/
Re: WAHP Fuel Limitation
Unfortunately, this is a current limitation.
However, in the VE2017 release the current fuels will be replaced by 'Energy end uses and meters'.
Under this scheme, a WAHP will have separate Heating energy meter and Cooling energy meter.
It will also be possible to distinguish between Space heating and Services water heating as the (heating) end use.
Regards
Donald
However, in the VE2017 release the current fuels will be replaced by 'Energy end uses and meters'.
Under this scheme, a WAHP will have separate Heating energy meter and Cooling energy meter.
It will also be possible to distinguish between Space heating and Services water heating as the (heating) end use.
Regards
Donald
IES Development Staff