Office controlled lighting profile

Part L2 of the Building Regulations (2006 edition).
Post Reply
btysoe
VE Graduate
VE Graduate
Posts: 86
Joined: Fri Mar 01, 2013 9:39 am

Office controlled lighting profile

Post by btysoe »

I have received a number of part L models from my colleague who routinely imports the annual profile template (Mod) office controlled lighting [LICO] and applies it as the dimming profile in rooms where there are dimmable fittings. Is this correct?

I see this as fundamentally wrong as the profile dims all lights within the zone to around 30% for the majority of the year giving fantastic energy savings. Where in reality most cases have just the first row of fittings nearest the windows as dimmable. (these are side light buildings without roof lights in the zone under consideration)

My preference is to use the NCM photoelectric controls
User avatar
Terence
Site Admin
Site Admin
Posts: 411
Joined: Mon Aug 25, 2008 12:58 pm
Location: Glasgow, UK
Contact:

Re: Office controlled lighting profile

Post by Terence »

No, I wouldn't say that is a suitable dimming profile for use in VE Compliance; if you're using the dimming profile option then the profile should accurately reflect the dimming operation of the sensor in the room. The following example of a suitable formula profile for dimming can be found in the ApPro user guide.

ramp(e1,0,1,500,.4) a formula suitable for applying as a dimming profile controlling lighting gain as a function of available daylight. It modulates the lighting gain as a function of the illuminance on the working plane, e1. The value of the profile falls from 1 at zero illuminance to 0.4 at illuminance 500 lux, thereafter remaining constant at this value. The value 0.4 (which you should set as appropriate) represents the fraction of the room‟s lighting gain which is not subject to daylight control. The illuminance e1 must be computed using the link to Radiance (a valid license key for Radiance is required)

If you don't want to use the Radiance link or don't have enough information on the operation of the sensor(s) in the room then you can use the Photoelectric options available under NCM Lighting Control.

I hope this helps.
Terence McMahon
IES Technical Support
Linkedin
btysoe
VE Graduate
VE Graduate
Posts: 86
Joined: Fri Mar 01, 2013 9:39 am

Re: Office controlled lighting profile

Post by btysoe »

Thank you Terence