Air supply temperature
Air supply temperature
I am looking at a building with a tempered air constant volume system for ventilation purposes. The main heating system in via underfloor. Currently I have the mechanical ventilation just assigned as Mechanical ventilation not an Apache system. Is thee any way of determining or setting the supply air temperature? Is so would I have to do this by making it an secondary system to input these parameters?
Your insight would be appreciated!
Your insight would be appreciated!
- Complex Potential
- VE Expert

- Posts: 467
- Joined: Wed Jan 09, 2013 11:57 am
- Location: Bristol, UK
Re: Air supply temperature
If you input the air as aux vent via the air exchanges tab you should be able to set the adjacent condition to "temperature from profile" and then apply an absolute profile which is set to your desired supply temp.