Dear all,
I would need an explanation regarding the definition of insulated glazing properties in IES-VE.
I made a test modeling 3 separated spaces with same size, same exposure and an only window exposed to south (without any shading/obstruction) with different solar properties:
-Insulated Glazing 1 (IG1) is completely clear to solar transmission (T=g_value=100%, out_R=in_R=0)
-IG 2 is modeled to obtain the same g_value of the manufacturer IG (IG 3), but in a simplified method (T=g_value=34%, out_R=1-g_value, in_R=0)
-IG 3 is modeled with manufacturer data: g_value=34% (T=32%, out_R=34%, in_R=34%).
Even if the g-values of IG2-IG3 are the same (and the total SC are very similar), comparing the solar gain results (in W, on hourly base) of a summer day (obtained by ApacheSim):
- Space 2 solar gains are exactly the 34% of those of Space 1’s (IG1, g_value=100%)
- Space 3 solar gains vary between 23-26% of those of Space 1’s
- Space 3 solar peak load is around the 50% of Space 2’s.
Comparing the solar gain results along the simulation year (in kWh):
- In winter months, Space 3 solar energy gain is about the 75% of Space 2’s.
- In summer months, Space 3 solar energy gain is about the 60% of Space 2’s.
Consequently, the question is simple: how should I model an insulated glazing?
I read the Construction Database User Guide (especially the Hints & Tips), but I’ve not found any answer.
Thank you in advance.
c
Insulated Glazing Properties_Simplified VS Manufacturer Data
Fast, accurate dynamic thermal simulation for energy/carbon modelling and much more...
Jump to
- Announcements
- Virtual Environment Software
- ↳ VE (For Engineers and Architects)
- ↳ ModelBuilder
- ↳ ModelIT
- ↳ Component Modeller
- ↳ DXF drawings
- ↳ Importing from SketchUp
- ↳ Importing from Revit®
- ↳ Solar
- ↳ SunCast
- ↳ Thermal
- ↳ ApacheSim
- ↳ ApacheCalc/Loads
- ↳ ApacheHVAC
- ↳ MacroFlo
- ↳ Vista
- ↳ VistaPro
- ↳ Utilities
- ↳ Templates
- ↳ Weather
- ↳ Profiles
- ↳ Constructions
- ↳ Apache Systems
- ↳ Compliance and Ratings
- ↳ ASHRAE 90.1 App. G - PRM
- ↳ Part L2 - England & Wales
- ↳ ApacheSim(DSM) Method
- ↳ SBEM
- ↳ Section 6 - Scotland
- ↳ Part F - Northern Ireland
- ↳ Part L - Republic of Ireland
- ↳ Title 24
- ↳ General building compliance
- ↳ Lighting
- ↳ FlucsDL/Pro
- ↳ Radiance
- ↳ General Lighting
- ↳ Value & Cost
- ↳ DEFT
- ↳ CostPlan
- ↳ LifeCycle
- ↳ Egress
- ↳ Simulex
- ↳ LISI
- ↳ Mechanical
- ↳ IndusPro
- ↳ Airflow-CFD
- ↳ MicroFlo
- ↳ VE-Gaia
- ↳ Plug-Ins
- ↳ Revit plug-in
- ↳ Latest Update
- ↳ Frequently Asked Questions
- ↳ Known Issues
- ↳ Wish List
- ↳ SketchUp plug-in
- ↳ Latest Update
- ↳ Frequently Asked Questions
- ↳ Known Issues
- ↳ Wish List
- ↳ License Keys
- ↳ Good Practice
- ↳ VE Python API
- VE Community
- ↳ Welcome to the boards
- ↳ General discussion
- ↳ Suggestions
- VE-Pro in French