If I have a VAV reheat system with radiant panels (modelled as radiator). How can I sequence them such that the radiant panels comes on first and then the reheat coil covers the rest of the heating load?
Thanks,
Francisco
VAV Reheat with Radiant Panels (Sequence)
-
Francisco_Contreras
- VE Newbie

- Posts: 4
- Joined: Fri Sep 08, 2017 7:09 pm
-
FrancescoMI
- VE Newbie

- Posts: 3
- Joined: Tue May 22, 2018 2:53 pm
Re: VAV Reheat with Radiant Panels (Sequence)
I would use a little bit different setpoint temperatures.
Suppose that the setpoint temperature for the radiant panels is 20°C. You can use 19.5°C as setpoint temperature for the VAV reheat coil. The VAV reheat coil will work only if the radiant system is not able to meet the 20°C setpoint temperature.
Suppose that the setpoint temperature for the radiant panels is 20°C. You can use 19.5°C as setpoint temperature for the VAV reheat coil. The VAV reheat coil will work only if the radiant system is not able to meet the 20°C setpoint temperature.
Re: VAV Reheat with Radiant Panels (Sequence)
I'd set the radiator controller setpoint a couple degrees higher than the VAV reheat, I think this would provide the results you want.