Lighting inputs

Post by ecoboost »

I am carrying out an SBEM analysis but when I view the lighting data box it does not let me select the lamp type, can you tell me how I can select this?
User avatar
Complex Potential
VE Expert
VE Expert
Posts: 467
Joined: Wed Jan 09, 2013 11:57 am
Location: Bristol, UK

Re: Lighting inputs

Post by Complex Potential »

Hi Ecoboost

I tend to use DSM more than SBEM but I'll give this a go.

Inside VE Compliance highlight a room and query it. Then go to the "Building Regs" tab and click on the "NCM lighting data" button.

At the top under SBEM design options select the "Only lighting type known" option and then the "Lamp type" drop down list directly beneath should become available which should allow you to select various generic fitting types.

Note: If you want to set multiple rooms at once to the same lamp type then you can go through the same process but use the "Edit group attributes" button instead of the "Query" button with multiple rooms selected.

Hope this helps.

CP
ecoboost
VE Student
VE Student
Posts: 39
Joined: Thu Aug 15, 2013 6:32 am

Re: Lighting inputs

Post by ecoboost »

Thanks CP, I found that but the lamp type is greyed out, think i'm missing something obvious here!
User avatar
Complex Potential
VE Expert
VE Expert
Posts: 467
Joined: Wed Jan 09, 2013 11:57 am
Location: Bristol, UK

Re: Lighting inputs

Post by Complex Potential »

That's odd.

Could it be that you are trying to assign lighting to an NCM zone type that is defined as un-lit? Just a thought.