Re: IES 2014 & Part L 2010 - Correct NCM Database?
Posted: Thu Nov 06, 2014 9:02 am
I've just thought of a little work around to get your absence detection back if you upgrade. If the room no longer allows you to put it as its greater than 30m2, you can make up the difference by changing the lighting diversity.
So set the room up as presence detection which allows you to account for parasitic power etc.
However this only gives an Foc factor of 0.9 and we are looking for 0.82. So set the diversity of the lighting to 0.82/0.9 = 0.911111..
You then get exactly the same result as you would have done with absence detection.
For Part L 2010, the notional building will also be correct as there are no occupancy controls. I'm not sure you can make a case for this in the new regs.
Ross
So set the room up as presence detection which allows you to account for parasitic power etc.
However this only gives an Foc factor of 0.9 and we are looking for 0.82. So set the diversity of the lighting to 0.82/0.9 = 0.911111..
You then get exactly the same result as you would have done with absence detection.
For Part L 2010, the notional building will also be correct as there are no occupancy controls. I'm not sure you can make a case for this in the new regs.
Ross