Re: Local Extract SFP not reported correctly BRUKL 2013
Posted: Thu Mar 29, 2018 3:08 pm
This still seems to be a problem, even though I have been told by IES support that it has been fixed.
For example, I am still getting SFP values reported in column B for rooms that have a centralised MHVR system with the SFP defined at zone level.
Or is it just that the BRUKL form doesn't have a column for reporting centralised MVHR SFP values? None of the options A-I seem to cover this. According to table 35 of the NDBSCG, the limiting value for such systems is 1.6 and the only column on the BRUKL that has 1.6 as the limiting value is E (Local MVHR system serving a single area) - ie not a centralised system.
I'm confused, and am having to hand over BRUKL sheets to the client with red data values on them, not ideal.
Jerry
For example, I am still getting SFP values reported in column B for rooms that have a centralised MHVR system with the SFP defined at zone level.
Or is it just that the BRUKL form doesn't have a column for reporting centralised MVHR SFP values? None of the options A-I seem to cover this. According to table 35 of the NDBSCG, the limiting value for such systems is 1.6 and the only column on the BRUKL that has 1.6 as the limiting value is E (Local MVHR system serving a single area) - ie not a centralised system.