Modeling Simple Corridor

Fast, accurate dynamic thermal simulation for energy/carbon modelling and much more...
Post Reply
ew0187
VE Student
VE Student
Posts: 30
Joined: Tue Jan 05, 2010 1:51 pm

Modeling Simple Corridor

Post by ew0187 »

I am trying to model a simple building, 1 floor. I just need simulate the natural ventilation through the corridor and a inner courtyard with a raised pyramid shaped ceiling. I have created the model in Google SkethUp, imported it to IES VE and created all the necessary requirements (to my knowledge) to simulate a natural ventilated space. But I keep on receiving an error message when I simulate " External holes are not permitted". I have recreated the building, systems, and simulation 3 times and i still get the same error message. Please let me know what i can do?
User avatar
David
Site Admin
Site Admin
Posts: 90
Joined: Mon Aug 25, 2008 12:56 pm
Location: IES Head Office
Contact:

Re: Modeling Simple Corridor

Post by David »

Hi,
You'll have an opening to the external... you need to make sure that it's a window or a door because the VE cannot handle unbound volumes. Assign an always open 100% profile within MacroFlo if you want to simulate a continually open entry.

Hope that helps.
David.
David, IES Technical Support
ew0187
VE Student
VE Student
Posts: 30
Joined: Tue Jan 05, 2010 1:51 pm

Re: Modeling Simple Corridor

Post by ew0187 »

i am trying to create both an courtyard (uncovered) and an courtyard(covered). the roof and floor both have hole, which i created for the courtyard(uncovered), you suggest i make that entire opening and in macroFlo set it as always opened?
ew0187
VE Student
VE Student
Posts: 30
Joined: Tue Jan 05, 2010 1:51 pm

Re: Modeling Simple Corridor

Post by ew0187 »

i am trying to create both an courtyard (uncovered) and an courtyard(covered). the roof and floor both have hole, which i created for the courtyard(uncovered), you suggest i make that entire opening and in macroFlo set it as always opened?

I tried your suggestions, all external holes i changed to windows and set them to always open. i still get the error message in ApacheSim. any other suggestions?
ZapBran
VE Expert
VE Expert
Posts: 315
Joined: Fri Apr 10, 2009 3:40 pm
Location: Manchester, UK

Re: Modeling Simple Corridor

Post by ZapBran »

don't want to state the obvious but...
...
...
...why are you creating a courtyard?
...
...
... that's an open space... the IES is for modeling rooms.
If you are looking for a cfd package to model wind movements in a valley or car park look for another software package.
You going to try simulating the pitch at Wembley next?

Model the building- not the open spaces between the rooms!
ew0187
VE Student
VE Student
Posts: 30
Joined: Tue Jan 05, 2010 1:51 pm

Re: Modeling Simple Corridor

Post by ew0187 »

i think you misunderstood what i meant. i am only looking to model the building. i have created a model of a single floor building, all one zone. there is a section of the building with a triangular shaped roof. the building is fully enclosed and i want to simulate with only natural ventilation. does that clarify the problem?
ZapBran
VE Expert
VE Expert
Posts: 315
Joined: Fri Apr 10, 2009 3:40 pm
Location: Manchester, UK

Re: Modeling Simple Corridor

Post by ZapBran »

sorry - 'uncovered' in my old mind meant no roof...

right...

you have no 'holes' on external planes? No openings on a wall... ceiling... floor?

Then you must have intersecting/clashing spaces... use the ModelIT check function to identify errors and address them.
User avatar
PCully
Site Admin
Site Admin
Posts: 1465
Joined: Tue Sep 09, 2008 9:52 am

Re: Modeling Simple Corridor

Post by PCully »

I'll jump in here to help out a bit more - if there are no obvious external holes then use the ModelIT Check (in ModelIT select the menu settings >> Model >> tick Surfaces (it's worth checking for intersections too) then click the Check button). This will launch a report and there will be a section highlighting geometry problems in the model including External Holes.

Sometimes External Holes can appear in a model as tiny slivers on surfaces, the report will help you track these down then it's just a case of finding them on the external surfaces and deleting them.

Phil
IES Worldwide Technical Support