Constant temperature boundary condition setting

Posted: Mon May 03, 2010 5:40 am
by geshen516
For external wall exterior surface, can I set the boundary condition to be constant temperature? for apache simulation.


Thanks and Regards
XiangJing

Re: Constant temperature boundary condition setting| solved

Posted: Mon May 03, 2010 6:47 am
by geshen516
geshen516 wrote:For external wall exterior surface, can I set the boundary condition to be constant temperature? for apache simulation.


Thanks and Regards
XiangJing
Just find the solution:Apache -> edit multiple adjacence

Re: Constant temperature boundary condition setting

Posted: Wed May 05, 2010 6:43 pm
by ZapBran
A little more for everyone else in the chance it might help.

In Apache:-
- select the room
- go down 1 level
- select the wall
- go down 1 level
- switch to adjacency mode
- hit the query button (got to be a betterword... 'properties' jumps out)
- Select 'temp from profile'
- et voila


now, notes:
1) you need to have defined the profile first
2) It has to be a value (or absolute) profile
3) The wall must be exposed (external)

Re: Constant temperature boundary condition setting| solved

Posted: Tue Jun 08, 2010 11:44 am
by huntervu28
geshen516 wrote:
geshen516 wrote:For external wall exterior surface, can I set the boundary condition to be constant temperature? for apache simulation.


Thanks and Regards
XiangJing
Just find the solution:Apache -> edit multiple adjacence
Is that "edit multiple adjacence" exist in VE5.9.2, please?

Re: Constant temperature boundary condition setting

Posted: Tue Jun 08, 2010 1:22 pm
by PCully
Hi,

The edit multiple adjacency button didn't exist in 5.9.2. You can still edit the boundary/adjacency condition but it will take a bit longer as you will have to do it for each surface individually.

1. Select the room in apache
2. go down a level of decomposition (blue down arrow) and select the surface
3. go down another level and change the dropdown from opening to adjacency
4. select the adjacency and click the query button on the apache toolbar
5. edit the adjacency

It's much easier in 6.0 (upgrade now if you can) but still possible in 5.9.2.

Phil

Re: Constant temperature boundary condition setting

Posted: Wed Feb 01, 2017 12:14 pm
by mwg
Does this also work for modelling internal walls as well?

Or solely external wall conditions?

Thanks in advance!