Macroflo opening profile

Posted: Sun Jul 18, 2010 7:13 am
by GARY JAMES
Hi, I've created a classroom an added a single window on one facade to analyse a Single sided ventilation strategy. I've successfully created a daily and weekly profile (say to open the window from 9am to 4pm mon - fri and close at all other times) in Apache but cant seem use this profile when defining the characteristics in in the Macroflo openings database. In the drop down menu I only get two options , on continuously or off continuously noticed the Apache profile icon on the side but I'm not to sure how to import the profile in the macroflo. Will be grateful for any help.

Cheers Gary

Re: Macroflo opening profile

Posted: Mon Jul 19, 2010 9:08 am
by PCully
Hi Gary,

Go into ApPro and ensure that you have saved a weekly modulating profile. As long as it is saved in ApPro Weekly Profiles then it will show up in the dropdown in MacroFlo.

Try experimenting with a few different profile types and you will see the list is populated after you save and exit ApPro.

Phil