I ran my simulation and do not get any consumption for lighting, though I've specified it. Is there some sort of link I am missing?
Thank you,
Lighting consumption
Re: Lighting consumption
Hi,
Have you set up a Lighting gain on your room data/thermal template internal gains tab? Check that this has a gain value and is set to a variation profile that comes on during the simulation period. You should then see this in the Vista building level (e.g. Total lights energy) or room level (lighting gains) results after the sim.
To see the lighting gains individually in Vista select "...internal gains breakdown" on the Simulation settings >> Output options.
Phil
Have you set up a Lighting gain on your room data/thermal template internal gains tab? Check that this has a gain value and is set to a variation profile that comes on during the simulation period. You should then see this in the Vista building level (e.g. Total lights energy) or room level (lighting gains) results after the sim.
To see the lighting gains individually in Vista select "...internal gains breakdown" on the Simulation settings >> Output options.
Phil
IES Worldwide Technical Support
Re: Lighting consumption
Thank you Phil, I will try it.
Re: Lighting consumption
It worked, thank you.