Apache Error

Post by Powerenergie »

Hi to all,

After modulate the whole building, I went to simulate the building with Apache Simulation, but in the beginnig this error happend "error:Maximum number of opaque types exceeded, 600"

How can I solve this error?


Thank you.
vajindarladdad
Site Admin
Site Admin
Posts: 217
Joined: Wed Sep 09, 2009 8:56 am

Re: Apache Error

Post by vajindarladdad »

Hi,
The problem is as the message suggests - there are too many constructions in the project database. You have to keep the number of constructions(+ materials) down to under 400.

To resolve this, you need to deleted all constructions apart from the ones you had assigned.

I hope this has been of some help.
Thanks & Regards ,