Posted: Thu Mar 03, 2011 12:27 pm
by cvrb2
Hi,
I have created several the daily&weekly profiles in APpro. They are "Absolute" profiles, not Modulating.
I was wondering how to tuse them in Building template manager>Room conditions>Heating profile. Because my problem in this menu "heating profile", only the Modulating profiles appear.

I didn't create any annual profil, is my problem linked to that?

Thank you for all the informations that you can provide me.

Regards

Re: Project Profiles in APpro

Posted: Thu Mar 03, 2011 2:25 pm
by PCully
Hi,

You don't need to define Annual profiles for this but you will require at least Weekly profiles before you can assign these in VE templates.

For this particular input it will only accept modulating profiles (0 means off and 1 means On). You might want to investigate the use of Absolute profiles to control the Set point though? Change the Setpoint dropdown from Constant to Timed and you will see you can apply Absolute profiles here.

Phil

Re: Project Profiles in APpro

Posted: Thu Mar 03, 2011 2:53 pm
by cvrb2
Thanks you for these information, it's really useful.