Hello,
I am running a criterion 3 compliance check but notice that some rooms in the attached model with glazing have a solar gain marked as N/A. Most of those rooms are circulation spaces.
Could you please let me know what is causing this?
Thank you for your help,
helena
Criterion 3 Check
- Complex Potential
- VE Expert

- Posts: 467
- Joined: Wed Jan 09, 2013 11:57 am
- Location: Bristol, UK
Re: Criterion 3 Check
Hi Helen
The reason is simply that Criterion 3 only appies to "occupied" or "mechanically cooled" spaces. Circulation zones fall outside of this definition and so do not get assessed.
The reason is simply that Criterion 3 only appies to "occupied" or "mechanically cooled" spaces. Circulation zones fall outside of this definition and so do not get assessed.