Hi,
One of our CFD consultants (Liam) has answered these queries and asked me to copy the response here (should be informative for other users as well):
It is not clear to me whether the "Import opening flow" option is somehow linked to Macroflo or not and how it works.
When you import opening flows Microflo reads a text file outputted by VE-VISTA. The text file is located in the VISTA subdirectory of your project and has the suffix "bcf" which stands for boundary condition file. This text files has
1) the temperatures of all the surfaces: ceilings, floors, walls, windows and doors.
2) the internal gains for people, lighting etc for each zone
3) Macroflo flows through openings in a zone, internal and external, cracks etc. The flow rates and the air temperature of the adjacency.
(3) comes from the Macroflo predictions.
Microflo will set up boundary conditions for each of the flows that lie along the boundary of the computational domain. If a flow is associated with an opening or crack inside the computational domain (away from the boundaries), e.g. a door between two zones when both zones are in the CFD model, then Microflo will not set up a boundary condition
If Macroflo predicts that flow enters the CFD domain through an opening then Microflo will set up a diffuser/supply boundary with the predicted flow rate and supply temperature. If Macroflo predicts that air exits the domain then Microflo will set up an extract boundary with the predicted flow rate.
Notice that the imported conditions, (1)-(3) above, does not include:
4) room conditioning/system stuff from the building template manager
5) air exchanges specified in the air exchanges tab in the building template manger.
These two extra items have to be set up manually. If you are using Macroflo then there might only be infiltration for (5) which will have only a small effect. (4) is very important to set up correctly. You can use the "convective plant load" from the VISTA results to work out how much heat or cooling is required to set up your CFD model to match the thermal model. Use the convective portion as the radiative portion goes into heating the room surfaces (well the vast majority anyway) which are already imported.
If my room has overpressure (more supply air then return), will Microflo calculate the airflow through windows/doors or is that in input it needs from Macroflo?
This question isn't easy to answer as
1) apacheSim/Macroflo doesn't include the physics to model pressurisation of a zone.
2) apacheHVAC/Macroflo has the physics but system data is not imported into Microflo so you still have things to setup manually anyway.
3) there are a number of ways to model mechanical ventilation, natural ventilation and mixed ventilation in the VE
In reality, if you are supplying air at a greater rate than extracting, the extra air leaks out of the building/zone somewhere until there is mass conservation, i.e. what goes in come out. Therefore if you are using apacheSim/Macroflo you can make an assumption of where the air leaks out. Usually the supply and extract rates are pretty close so you can just increase the extract rate from the boundary(s) that represent the extract for your system. OK all the air that would leak out of window cracks, under doorways, etc., is then assumed to exit the extract(s) but if the supply and extract rates are close this assumption will be fine.