In the NCM 2010, the fan power density of "VAV System" is based on Equation 9:
FPS = Max (FAR_max , SCR) x SFP
FAR: Peak fresh air supply rate set by NCM
SCR: Space conditioning supply rate
where SCR = Max ( PSH , PSC) / (p * Cp * deltaT)
PSH/PSC: Peak space heating/cooling load
My question is, how does IES calculate the PSH and PSC? If the PSH/PSC figures are based on the dynamic simulation, I would expect the "peak" figure taken would be in one morning hour, which is usually two to three times larger than the normal load as the ApCalc assumes an infinity plant size in the "heat up" hour.
Could IES clarify the issue?
Regards
Howard
In the NCM 2010, the fan power density of "VAV System" is based on Equation 9:
FPS = Max (FAR_max , SCR) x SFP
FAR: Peak fresh air supply rate set by NCM
SCR: Space conditioning supply rate
where SCR = Max ( PSH , PSC) / (p * Cp * deltaT)
PSH/PSC: Peak space heating/cooling load
My question is, how does IES calculate the PSH and PSC? If the PSH/PSC figures are based on the dynamic simulation, I would expect the "peak" figure taken would be in one morning hour, which is usually two to three times larger than the normal load as the ApCalc assumes an infinity plant size in the "heat up" hour.
Could IES clarify the issue?