Auto sizing custom HVAC

Posted: Thu Jun 16, 2011 8:57 am
by myope
I dun know exactly Apache "ASHRAE Loads" can sizing fan(s) and coil(s) for a custom HVAC system. It seems work only with coil(s).

Auto sizing base on Leed PRM works very well on prototype system, but doesn't work on custom system, especially with flow and fan(s).

Any advice will be appreciated!

Re: Auto sizing custom HVAC

Posted: Fri Jun 17, 2011 1:13 pm
by PCully
Hi,

Autosizing can only be done with the Prototype systems at the moment so custom networks will need to be sized manually.

Sorry
Phil

Re: Auto sizing custom HVAC

Posted: Sat Jun 18, 2011 6:28 am
by myope
Thank Phil,

Re: Auto sizing custom HVAC

Posted: Thu Jun 30, 2011 1:12 pm
by PCully
this is maybe one you'd have to get on to Support and ask as I'm not sure how it should work for PRM.

To switch off the autosizing when running the Loads calcs it should simply be a case of unticking the "Update ApacheHVAC system sizes?" checkbox on the ASHRAE Loads settings dialog but I don't even know if you have control over that for the Baseline and Proposed systems?

Sorry I'm not a great deal of use here

Phil

Re: Auto sizing custom HVAC

Posted: Wed Oct 12, 2011 10:42 pm
by luanaepb
Hi,

I am having some problems in understanding how do the ApHVAC/ApacheLoads work.

For example, I want to obtain the flow rate necessary to a zone to a certain condition of internal gains, solar gains, etc.

Apparently, it is not possible to autosize the flow. Can you confirm this to me, please?

Currently, I am using the version 6.4.0.6

Thank you.

Re: Auto sizing custom HVAC

Posted: Thu Oct 13, 2011 2:58 pm
by myope
Each predefined HVAC system in IESVE has a conjunction with some exel file that contents flow calculation formula, following ASHRAE 62.1 (2007 - I suppose)
Thus, ApHVAC can not auto reside custom HVAC fan flow because of lack excel formula file.

In some case, we see ApHVAC resizes flow because preset flow is higher than flow demand in simulation, it doesn't mean ApHVAC follows ASHRAE 62.1.

Re: Auto sizing custom HVAC

Posted: Fri Oct 14, 2011 2:53 am
by luanaepb
Thank you for your answer.

I just don't understand how to run one sizing run in ApHVAC, i.e, I have one zone, with a certain cooling load and I want to discover the value of the air flow that corresponds to this cooling load.

Do you have any suggestions?

Thanks.

Re: Auto sizing custom HVAC

Posted: Sun Oct 16, 2011 10:15 am
by myope
It's base on Cooling load and Air Flow calculation after realizing Ashrae load.