Best way to model 1 floor only for loads

Posted: Wed Feb 15, 2012 11:35 am
by bootsam
If i have a multi story building and i only need the loads for one intermediate floor. How is it best to model the ceiling and floor? Should i create a dummy space above and below, ie another floor. Or is there an easy way to set temps across the floors and ceilings.

Ta.

Re: Best way to model 1 floor only for loads

Posted: Thu Feb 16, 2012 1:03 pm
by JohnLloyd
Draw a dummy floor above and below and then set them to be of type 'Adjacent Building'. The intermediate floor and ceiling will then be treated as adiabatic (i.e. no heat transfer).

Re: Best way to model 1 floor only for loads

Posted: Thu Feb 16, 2012 3:45 pm
by bootsam
Cant I just use the 'edit multiple adjacancies' to put a temp on the ceilings and floors? Gotta be easier or is there something wrong with this way.

Re: Best way to model 1 floor only for loads

Posted: Fri Feb 17, 2012 11:48 am
by JohnLloyd
You can, and it will probably give you similar answers, but that method will result in both the floor and ceiling of your single floor being unshaded.

This is probably not a huge issue but I think it will make the thermal mass within those constructions act differently due to the additional flux hitting their outside surfaces.

That would only be an issue in a dynamic simulation and shouldn't impact any steady state calcs.

Re: Best way to model 1 floor only for loads

Posted: Fri Feb 17, 2012 4:46 pm
by bootsam
Thanks John. Its only a steady state calc i am after. But I just needed confirmation that i can use both methods. Generally i dummy a floor but wondered whether i could use the adjancies instead.