Posted: Sat Mar 17, 2012 4:16 pm
by Richardo1505
Hi all,

Can anyone offer some good advise how best to measure fresh air distribution in a space using MicroFlo, as such to inform a judgement regarding indoor air quality a different points in the room. thanks all,

Re: CFD Fresh Air Distribution

Posted: Tue Mar 27, 2012 7:49 am
by liamh
How about using the age of air and air change effectiveness variables? Or if there are people in your model, the concentration of CO2?

Re: CFD Fresh Air Distribution

Posted: Tue Mar 27, 2012 8:08 am
by Richardo1505
I'm not sure you can measure C02 with Microflo. I know you can with Macroflo

Re: CFD Fresh Air Distribution

Posted: Tue Mar 27, 2012 8:18 am
by liamh
You can. If your apacheSim/macroflo model has occupants then their CO2 production is automatically imported into Microflo and gets spread over the whole zone volume - from floor to ceiling height.

If you don't like that simplification you can add non-solid source components that release the same amount of CO2. Then you can control where the CO2 is released rather than use the default - over the whole zone.

Re: CFD Fresh Air Distribution

Posted: Tue Mar 27, 2012 8:24 am
by Richardo1505
ok thanks, I'll give it a go