Re: atrium window and holes
Posted: Fri Oct 09, 2009 9:28 am
You can't have external holes. Apache is doing calcs on closed spaces.
Replace your hole with a door and open it 100% of the time.
It's the same as if you were modelling vent-louvres.
Atrium window will be external if it's on an external wall... if you think it's internal then I'd imagine you've got some dodgy intersecting geometry (fix it).
Replace your hole with a door and open it 100% of the time.
It's the same as if you were modelling vent-louvres.
Atrium window will be external if it's on an external wall... if you think it's internal then I'd imagine you've got some dodgy intersecting geometry (fix it).