Page 1 of 1
ASHRAE Navigator- Failed to load HVAC network
Posted: Fri Dec 07, 2012 6:49 pm
by Nirhalfon
Hello,
When I do the System load calculations in the sizing runs I keep getting an error ,message 'Failed to load HVAC network'file and then the pathway to 270Deg baseline
The result files, obviously, show 0 in all values
Why could that be?
Nir
Re: ASHRAE Navigator- Failed to load HVAC network
Posted: Fri Dec 07, 2012 7:02 pm
by PCully
I'm not sure what would cause this but maybe some error occurred which meant the variants were never created, you may need to step further back through the Navigator (maybe to Generate Baseline, perhaps even further) to make sure they are generated properly so that when you run the sizing calcs everything is ready for each load calc etc
Phil
Re: ASHRAE Navigator- Failed to load HVAC network
Posted: Fri Dec 07, 2012 11:16 pm
by Nirhalfon
Thanks,
The cause was Dropbox which was syncing the files as they were created and restricted access to them.
Best,
Nir
Re: ASHRAE Navigator- Failed to load HVAC network
Posted: Mon Dec 10, 2012 12:15 pm
by PCully
that's odd, I've not heard of that before.
Has anyone else experienced this? For reference what did you do to resolve?
Phil
Re: ASHRAE Navigator- Failed to load HVAC network
Posted: Tue Mar 05, 2013 8:53 am
by Nirhalfon
I paused the sync on dropbox while running the calculations.
Problem solved.
Nir