Re: Displacement (stratified) Ventilation
Posted: Fri Aug 07, 2009 9:53 am
Hi there,
Just a quick entry to give you a start...
To model a displacement system in an auditorium you will need to zone the space vertically to account for the stratification of the air and use MacroFlo combined with ApacheHVAC to model the displacement system.
I'd recommend that displacement systems are simulated by dividing the room into two levels:
1. An occupied level up to 1.8m and
2. An upper level representing the remainder.
The system air is supplied at low level and passed on to the upper level.
As a rule of thumb, convective gains occurring in the lower level from people, equipment or lights should be apportioned between the levels in the ratio 1/3 to the lower level and 2/3 to the upper level. This ratio reflects the tendency of the warm air to rise in plumes.
The 2/3 ratio must be added as a watts figure as opposed to W/m2, as holes and windows in a floor reduce the calculated watts. Therefore a floor with a 100% hole (or window) will result in no watts from a W/m2 entry.
If you have a Plenum:
You can set up a proportional control on your HVAC network to sense the return air temperature. This will allow you to vary the supply air temperature into the plenum. Make sure you check the admittance values for the construction assigned to the plenum and also check the internal surface resistance values to ensure that they are suitable for your calculation.
You can calculate the peak and cooling loads using CIBSE loads calculation. Make sure you have the correct ventilation rates, constructions and internal gains assigned.
Hope that helps,
David.
Just a quick entry to give you a start...
To model a displacement system in an auditorium you will need to zone the space vertically to account for the stratification of the air and use MacroFlo combined with ApacheHVAC to model the displacement system.
I'd recommend that displacement systems are simulated by dividing the room into two levels:
1. An occupied level up to 1.8m and
2. An upper level representing the remainder.
The system air is supplied at low level and passed on to the upper level.
As a rule of thumb, convective gains occurring in the lower level from people, equipment or lights should be apportioned between the levels in the ratio 1/3 to the lower level and 2/3 to the upper level. This ratio reflects the tendency of the warm air to rise in plumes.
The 2/3 ratio must be added as a watts figure as opposed to W/m2, as holes and windows in a floor reduce the calculated watts. Therefore a floor with a 100% hole (or window) will result in no watts from a W/m2 entry.
If you have a Plenum:
You can set up a proportional control on your HVAC network to sense the return air temperature. This will allow you to vary the supply air temperature into the plenum. Make sure you check the admittance values for the construction assigned to the plenum and also check the internal surface resistance values to ensure that they are suitable for your calculation.
You can calculate the peak and cooling loads using CIBSE loads calculation. Make sure you have the correct ventilation rates, constructions and internal gains assigned.
Hope that helps,
David.