Part L2 Compliance include Louvers?

Part L2 of the Building Regulations (2006 edition).
Post Reply
RossThompson87
VE Professor
VE Professor
Posts: 202
Joined: Mon Feb 13, 2012 8:56 am

Part L2 Compliance include Louvers?

Post by RossThompson87 »

Hi,

Should louvers be included when doing a Part L2 compliance model?

It appears the notional building doesn't make allowance for them. Is this mentioned in any documents?

Thanks

Ross
User avatar
PCully
Site Admin
Site Admin
Posts: 1465
Joined: Tue Sep 09, 2008 9:52 am

Re: Part L2 Compliance include Louvers?

Post by PCully »

Hi Ross,

The Notional won't have any local shading, that's a feature that the actual building can benefit from. This is described in the NCM Modelling Guide, usually a good starting point for regs questions.

Phil
IES Worldwide Technical Support
JohnLloyd
VE Professor
VE Professor
Posts: 173
Joined: Tue Oct 05, 2010 8:51 am

Re: Part L2 Compliance include Louvers?

Post by JohnLloyd »

You mean ventilation supply / extract louvres?

I don't think there's a definitive answer to that anywhere, but I suspect the intention is for them to not be drawn into the Part L model but for their U-value to be included within the building average wall U-value calculation. I very much doubt that ever happens though.
User avatar
Complex Potential
VE Expert
VE Expert
Posts: 467
Joined: Wed Jan 09, 2013 11:57 am
Location: Bristol, UK

Re: Part L2 Compliance include Louvers?

Post by Complex Potential »

NCM Modelling Guide 2010 Pagagraph 30:

"Smoke vents and other ventilation openings such as intake and discharge grills must be disregarded in the Actual, Notional and Reference buildings, and their area substituted by the relevant opaque fabric (ie. immediately surrounding roof or wall)."